I try to copy and past again:
http://www.tango-controls.org/media/filer_public/bf/e2/bfe2d3ed-d284-4cd1-9f48-7bed2a809321/alarmtesttar.gz

but in any case it is taken from http://www.tango-controls.org/community/projects/alarm-system/ under "Downloads"
Hi,

the link works for me. Thanks!

Andy
Hello all

I am getting errors while opening alarm-gui.
I have configured the alarm,alarmtest device server and alarm-gui.
I may have configured it wrong.

Please find the attached Jive configurations for alarm and alarm-test device server and the errors which come while opening alarm-gui.

Thanks and Regards
Anshul Soni

You are specifying in the command line that your alarmtest device is in ecrfpsa/alarmtest/0.
Do you have configured in jive the device with that name and launched it ?
In any case it is needed only to test event subsystem in the "Test" tab.
Apart from that it looks ok, you can try to add the configuration of a new alarm and test that.

Graziano
I have configured the alarmtest device in jive as ecrfpsa/alarmtest/0. I have attached the image of the same above.
Where is the place to add new alarm ?
Could you please share your device server configurations?
Could you please share your alarm-configurations/rules for exploring purpose ?
Also what are the pre-requisites to load alarm gui ?

Thanks and Regards
Anshul
The configuration of the device properties of alarmtest is wrong: it has no device property
But in any case this is not the reason it is not working.
I cannot see from your screenshot if you have launched the alarmtest device server before launching the gui:
"alarmtest-srv alarmtestsrv" looking at your configuration.

To load a new alarm you have to execute the Load command with a configuration string like:
"ecrfpsa/alarmtest/0/fault (ecrfpsa/alarmtest/0/state == FAULT) 0 fault -1 gr_all \"AlarmTest fault\" ;"
if you want to configure an alarm when the State of ecrfpsa/alarmtest/0 for example is in FAULT


Graziano
 