PyPLC communication with siemens
|
|
---|---|
When im running the device server pyPLC ,the server cannot recognize the plc ,i do all the required steps to etablish the modbus communication but nothing change i don't know what's the problem ? |
|
|
---|---|
The PyPLC is an attribute mapping layer on top of Modbus C++ device server. Have you been able to configure the Modbus device? Once you configured it, try if any of these calls returns any value: ds = PyTango.DeviceProxy('your/modbus/device') ds.ReadHoldingRegisters([0,10]) ds.ReadInputRegisters([0,10]) |